Saved Bookmarks
| 1. |
The neutral of a 10 MVA, 11 kV alternator is earthed through a resistance of 5 Ω. The earth fault relay is set to operate at 0.75 A. The CT's have a ratio of 1000 : 5. The percentage of alternator winding unprotected is _______%.11.8 |
Answer» The neutral of a 10 MVA, 11 kV alternator is earthed through a resistance of 5 Ω. The earth fault relay is set to operate at 0.75 A. The CT's have a ratio of 1000 : 5. The percentage of alternator winding unprotected is _______%.
|
|