A 3-phase alternator has synchronous reactance, Xd=1.7241p.u. and is connected to a very large system. The terminal voltage is 1.0∠0∘p.u. and the generator is supplying to the system a current of 0.8 p.u. at 0.9 power factor lagging. If the real power output of the generator remains constant but the excitation of the generator is increased by 20%, then the Q delivered to the bus by the generator is ____p.u. (Answer upto three decimals).0.632

Answer» A 3-phase alternator has synchronous reactance, Xd=1.7241p.u. and is connected to a very large system. The terminal voltage is 1.00p.u. and the generator is supplying to the system a current of 0.8 p.u. at 0.9 power factor lagging. If the real power output of the generator remains constant but the excitation of the generator is increased by 20%, then the Q delivered to the bus by the generator is ____p.u. (Answer upto three decimals).
  1. 0.632